Dear annupalani, In both SIEMENS PLC's you need to include the DP/DP coupler in HW configuration. It is a DP slave with an unique profibus address. It can be different DP slave address on both HW-configurations. Then you will have to configure the amount of Bytes you want to communicate between the PLC's Here is a link to manual: DP/DP coupler Best regards, Wizard |