(0)| 12/30/2009 10:57 AM | |
Posts: 1742 Rating:
Hello, If you mean SIRIUS Softstarter, you should find it in your HWConfig Catalog. See annex. You will find the system manual here: http://support.automation.siemens.com/WW/view/en/21772518 Chapter 8 explains the Profibus communication. Configuration can be done via Softstarter ES. AttachmentSirius.pdf (615 Downloads) |
| 1/2/2010 11:21 PM | |
Joined: 9/27/2006 Last visit: 12/28/2025 Posts: 12477 Rating:
Hello zmzm; To follow up on Ayman's post, the gsd file you are using corresponds to the ABB fieldplug (which we have used on some of their units, including softstarters). Here, from the ABB site, is the technical description of the fieldplug and the data structure it can use when connected to a DP-Master:for Profibuys data exchanges. http://library.abb.com/GLOBAL/SCOT/scot209.nsf/VerityDisplay/97361B3E83A1DE8AC12571AE0023D771/$File/2CDC192001D0208.pdf Hope this helps, Daniel Chartier |
| 1/4/2010 2:34 PM | |
Hello zmzm; The selection of the modules (andinput/output registers for Profibus-DP exchanges) is done through the HWConfig editor, by selecting the slave(s) in the Profibus catalog (once the gsd file is loaded into the configurator) and dragging it to the Profibus-DP bus line. You then add "modules" to the slave's address area, that represent blocks of inputs or outputs as required by your dtat exchange structure; the permittes size of these modules was defined by the manufacturer in the gsd file you imported,. You have to know that the CP 342-5 works differently than the integrated DP interface (on the CPU). Once the Profibus configuration is loaded to the CP, it works autonomously, collecting the Profibus data from its slave(s); but the communication between the CPU and the CP requires special blocks that you must program in your application, DP_Send and DP-Recieve. Look at the following FAQ, it has a lot of information on what you should pay particular attention to when you work with a CP 342-5 as DP-master: http://support.automation.siemens.com/WW/view/en/18208090 Also, search for CP 342-5 in the forum,'s search box; this subject has been broached many times, and you might find some information there that could make your life easier. Hope this helps, Daniel Chartier |