(0)| 1/18/2010 4:13 PM | |
Posts: 73 Rating:
Hello FunStuff, Generally speaking chemical applications are based on Process Safety standards such as IEC61511. They are normally Low Demand mode [PFD] applications and therefore are not calculated in the same way as High Demand mode applications [Machine Safety, PFHd]. The definition for Low Demand based on IEC62061"eg frequency of demands on a safety system is no greater than one per year and no greater than twice the proof-test frequency." The SET calculates SIL based on IEC62061 which is High Demand Mode of operation for machine applications. Please look at the following links they might help http://support.automation.siemens.com/WW/view/en/35444324 www.siemens.com/process-safety |
| 1/18/2010 5:48 PM | |
Posts: 103 Rating:
I havethree excellentSiemens documents that I found and according to those it would seem that my systems need to be a PL C or SIL 1. This is very achieveable with a 3RK3 system but I need to perform the calculation on a pressure sensor using the factory data to see what subsystem SILCL is. One of the documents has many examples but I either missed or am failing to find the correct way to take a non-safety rated device (pressure switch) and perform an evaluation on it to determine the SILCL of the subsystem. Do you have any examples of this calculation for a non-safety rated device? I have attached one of the documents.
AttachmentSafety Design Siemens Example Doc.pdf (1408 Downloads) |