As far as I understood manual SIMATIC S7-300/S7-400 Software redundancy for SIMATIC S7 manual both CPUs can run two different programs (they are executed in OB1). They also have redudant part of programs (executes in OB 35). But it is still not clear for me, if I can read information from my ET200 by both of rhem in non-redudant part of programs? |
| 12/21/2010 3:21 PM | |
|
Joined: 7/2/2008 Last visit: 12/21/2025 Posts: 929 Rating:
|
Hello ssantiago, Yes you can read theinput data from ET200Minthe non redundant section of user program (in both CPUs). Best regards. H-H |