(0)| 12/23/2010 7:48 AM | |
Joined: 4/14/2010 Last visit: 6/26/2025 Posts: 525 Rating:
GOOD MORNING SIR I HAVE PROBLEM WITH CPU416 ITS EXTERNAL FAULT LED CONTINUE STILL BUT CPU IN RUNNING MOD MACHINE ALSO HAVE WORK PROPERLY EXCEPT KS800-DP ONE MODULE KS800-DP IS FAULTY I HAVE REPLACE THIS BUT STILL FAULTY MESSAGE APPEAR IN HW_CONFIG. THE CPU 416 DURING RUN MOD SUDDENLY GO TO IN STOP MOD AND ALL LED's (Interna fault,external fault,stop,run) CONTINUE FLASHING THEN I DO THE POWER SUPPLY OFF AFTER 5 MINUTE POWER UP THE CPU THEN IT HAVE AGAIN RUN MOD AND HAVE PROPERLY WORK AFTER SOME DAYS IT HAVE AGAIN THIS FAULT (and i also revise the power off procedure then it have again RUN mod) SIR I HAVE ATTACHED ON-LINE SNAPS KINDLY CHECKED IT IS THE FIRMWARE PROBLEM WITH CPU..???? IS THE PROBLEM WITH KS800-DP I HAVE ONE KS800-DP SPARE BUT HOW CAN I CONFIGURE IT FOR THERMOCOUPLE OR PT100 AND NOD ADDRESS 8 & 9...??? I HAVE ALSO DISABLE THE KS800-DP FROM PROFIBUS 1 DP MASTER NOD 8 & 9 BUT CPU EXTERNAL FAULT STILL BUT HAVE RUNNING MOD...??? KINDLY RESOLVE THIS PROBLEM.. THANKS REGARDED AttachmentCPU416.zip (381 Downloads) |
MS |
| 12/23/2010 8:11 AM | |
Joined: 3/21/2006 Last visit: 10/16/2025 Posts: 10239 Rating:
Hello, I think this isn't a problem with CPU. In diagnostic buffer is mentioned Address 110 and FC779. What do you have there? As I saw you don't have this address. About KS800 DP settings, just use Multi Temperaturecontroller KS800 manual. There have also example... PLEASE, MAKE CAPS LOCK OFF! COMMON... Best regards, Hristo Mihalev |