(0)| 7/29/2013 10:50 PM | |
Joined: 9/27/2006 Last visit: 12/30/2025 Posts: 12477 Rating:
Hello arain; The CB24 is a very old module, and information is not so easy to retrieve. Look at the following documents: Simoreg K 6RA24 Communication board CB24 operating instructions F-1.0 PROFIBUS-DP Protocol Introduction Both of them indicate what parameters mudt be set for Profibus-DP comms with the Simoreg drive. The second one shows a Reverse signal available on PZD Word E3 (Control Word 2). See the attached document. And you will require a gsd file to integrate this Profibus slave in the HWConfig Profibus configurator.With thanks to our friend KSN:
Last edited by: O_Moderator at: 7/30/2013 7:47 AMattachment reattached Last edited by: dchartier at: 7/29/2013 10:53 PMLast edited by: dchartier at: 7/29/2013 10:51 PM |
| 7/30/2013 7:39 AM | |
Joined: 8/25/2006 Last visit: 12/30/2025 Posts: 2221 Rating:
Hello, dchartier. It looks like the second document is a part of manual for winder application using 6RA24+CB24+Technology board, wherePZD Word E3 (Control Word 2) is sended from master to the Technology board, but not to the drive. In standard configuration of 6RA24+CB24 there is no any Reverse bit in control word. Hello, arain. If your drive is 4Q, then you can simply inverse speed setpoint in the PLC program. If your drive is 1Q, then you can use BIF57 andConverter Specific Control Word STWF. Refer to themanual, chapters 10.3.57 and 10.5.2. |
| 8/1/2013 1:29 PM | |
Posts: 61 Rating:
can you provide me any samle program of profibus communication of s7-300 to simoreg 6ra24 via CB24. program with control word addressing.PPO3 and PKW PPO1 |
| 8/2/2013 11:54 AM | |
Hello. 4096d = 1000H -4096d = F000H Also look at the attached picture. |
| 8/5/2013 1:04 PM | |
Posts: 61 Rating:
problem have been slove i chnage P074 to 0x2 (4 quard ) it works in default setting it was set as 0x1 (1 quard )