(1)| 1/13/2016 10:14 PM | |
|
Posts: 34 Rating:
|
Using 0BA6 8I and 3Q Any I closes Q1 4 or more I closes Q2 The simulation works perfectly. However, two commissioned devices randomly fail to count the inputs. I've duplicated the error on the test bench. Could I have 2 faulty devices? Or could it be an AM or AT function block error? The actual program is considerably more elaborate...I've loaded just the basics in an attempt to troubleshoot the problem...without success. Ideas? Thanks for looking. AttachmentBoilerStageFiredControl.pdf (362 Downloads) |
| 1/14/2016 2:59 PM | |
|
Posts: 34 Rating:
|
Forum Rookie mistake AttachmentBoilerStageFiredControl.zip (293 Downloads) |
| 1/14/2016 3:02 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
|
| 1/14/2016 3:18 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
Do those logos showing the error, fast counter inputs (I3-I6)? |
| 1/14/2016 3:26 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
Although I have only one 0BA8, but since it appears that the fast counter inputs not so with the counters works as the other four inputs. Show at the attached video to see the difference between simulation and online monitoring. AttachmentTest.wmv (287 Downloads) |
| 1/14/2016 3:56 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
Here my solution for your Problem.
AttachmentBoilerStageFiredControl_V2.zip (293 Downloads) |
This contribution was helpful to
|
|
| 1/14/2016 5:32 PM | |
|
Posts: 34 Rating:
|
Outstanding! Thank you for your assistance. I'll give it a real world test this afternoon. |
This contribution was helpful to
|
|
| 1/14/2016 10:43 PM | |
|
Posts: 34 Rating:
|
ixo65, With your revision, my device works as expected. Thanks again for your assistance. |
This contribution was helpful to
|
|
| 1/14/2016 10:54 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
Hello L L, you are welcome. |