(0)| 3/15/2017 2:23 PM | |
|
Joined: 12/18/2014 Last visit: 1/2/2026 Posts: 36395 Rating:
|
In the attachment a possible solution. The process is started with I1. The analog comparator compares the signal from the load cell with the signal setpoint. As long as the signal from the load cell is smaller than the setpoint, the pump is running. Attachmentweighing.zip (356 Downloads) |
Follow us on