Hello akbar; The following application example should provide you with most of what you need to use a S7 F-CPU with F/IO; the main difference is that the F/IO are part of an ET 200S station over Profibus-DP, instead of being part of the central rack,. But the philosophy and the Safety functions are the same. Safety: Passivation and Reintegration of F/IO https://support.industry.siemens.com/cs/ww/en/view/22304119 Hope this helps, Daniel Chartier |
| 5/8/2018 12:13 PM | |
|
Joined: 9/27/2006 Last visit: 12/27/2025 Posts: 12474 Rating:
|
Hello akbar; Your CPU is a S7-315F-2PN/DP, based on your initial query. To program Safety functions on this CPU you need a package named Distributed Safety: https://support.industry.siemens.com/cs/us/en/view/54110126 You seem to be trying to use a FH-system package, based on CFC blocks, that can only program Safety functions on S7-400HF PLCs. Hope this helps, |