(0)| 12/11/2018 2:30 PM | |
|
Joined: 5/6/2010 Last visit: 1/5/2026 Posts: 2047 Rating:
|
Hello, you should connect your signal between the isolator and the PLC to ground. regards
|
| 12/12/2018 7:36 AM | |
|
Joined: 5/6/2010 Last visit: 1/5/2026 Posts: 2047 Rating:
|
Hello, if you have a lightning strike then you have a overvoltage at the input of your transducer. Your trancducer have a maximum voltage (normally up to 1..2 kV) to protect the input/output. If you need a lightning strike protection then you need additionally a surge protection like this Surge protection device - TTC-6P-1X2-F-M-24DC-PT-I
|