(0)| 12/7/2008 12:12 PM | |
Joined: 10/7/2005 Last visit: 12/29/2025 Posts: 3052 Rating:
Check also if you have the terminator module connected to the right side of the last ET200S I/O card. This terminator module (part number 6ES7 193-4AJ00-0AA0)is supplied together with the IM151 but commonly "forgotten" to be clicked onto the last I/O card in the ET200S station (in which case you'll also get the actual vs present configudation mismatch problem that you described). As for how to wire the I/O cards up, have a look at these manuals which you can downlaod from the Siemens service and support web (and note the role that the terminal modules plays): - ET200S Operating Instructions - ET200S Distributed I/O system I hope this helps. |
Cheers |
| 12/10/2008 11:26 PM | |
Posts: 3 Rating:
all the numbers and all the letters are the same that there are written in the devices
| 12/17/2008 1:51 AM | |
Hello larrydesu01 please find the requested picture attached. I hope this helps and merry X-Mas |
Cheers |
