(0)| 10/21/2020 3:31 PM | |
Joined: 12/28/2016 Last visit: 12/14/2025 Posts: 435 Rating:
Hi H-System with Redundant Sample Project |
https://pnap.ir |
| 10/21/2020 3:37 PM | |
Joined: 9/27/2006 Last visit: 12/31/2025 Posts: 12479 Rating:
Hello; The equipment you plan to use consist of a split rack (2x9-slot rack for redundancy), a S7-400H redundant CPU and a standard power supply (4A, 120/230 V). This is the required basis of a S7-400 H system, as defined in the manual for S7-400H: You will need also special fiber optic cables and connectors to implement the redundancy between the 2 CPUs. https://support.industry.siemens.com/cs/ww/en/view/82478488 Hope this helps, Daniel Chartier |
| 10/22/2020 9:34 AM | |
Posts: 8 Rating:
Yes, you're right I meant what you wrote exactly Thanks so much for your reply, it was really helpful |
