Posts: 22 Rating:
|
Dear All, There is an phase rotation protection parameter avaible in switch ES. How does the breaker know the change of phase rotation? Regards, Santoo........ |
6/24/2009 6:11 AM | |
Posts: 262 Rating:
|
Hi santosh, I'm with Navnag for the same in addition to that i would like to send you the file as attached from the manual. Hope your query is replied with this. AttachmentDoc1.zip (444 Downloads) |
5/24/2014 9:33 AM | |
Posts: 235 Rating:
|
dear all, I cant understand wahat you are said this facility available in every CB? |
5/24/2014 12:49 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
This function is only available with the option "Metering Plus" Function for 3WL ACBs. Pl see attachment. It is not a part of the standard ETU functions. Hope this helps Cheers Navnag AttachmentSENTROL_3WL_Metering_Function_Plus.pdf (522 Downloads) |
There is no such thing as the last bug in a program |
|
5/26/2014 2:28 PM | |
Posts: 235 Rating:
|
Dear all, for extended function fcility in WL pls find the attachment this will help you..... AttachmentSentron WL Datasheet.pdf (407 Downloads) |