5/22/2014 8:49 PM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, It is normal when connecting adapter to your PC, leds wouldn't lit if the PLC side is disconnected. This PC adapter fed from Automation System, leds will lit when connecting the PLC side (Sub-D 9 pin socket) into the CPU. This PC adapter6ES7972-0CB20-0XA0can work with MPI or Profibus up to 1.5Mbps baud. If you connected the PC adapter to a profibus network with baud rate setting more than 1.5Mbps, you will not be able to communicate with the CPU. I recommend for you to connect the CPU via its MPI interface. Or you can use this adapter "6GK1571-0BA00-0AA0" which can work withMPI or Profibus up to 12 Mbps baud Hope this helps. |
Ayman Elotaify |
|
This contribution was helpful to
1 thankful Users |
5/23/2014 7:40 AM | |
Posts: 5 Rating:
|
OK. Thanks. Yes I am trying to connect to the backside of the Profibus connector on the OLM which is down stream of the actual PLC (CPU 317). So will this adapter not work for that6ES7 972-0CB20-0XA0. The Profibus connector on the CPU is not open so Im not able to connect to the CPU with the6ES7 972-0CB20-0XA0at that point. Thanks again.
|
5/23/2014 7:57 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, If you could change the bus connector with PG socket you will be able to connect the PC adapter to Profibus DP port of the CPU.
|
Ayman Elotaify |
|
This contribution was helpful to
1 thankful Users |
5/23/2014 8:22 AM | |
Posts: 5 Rating:
|
Im not able to change out the connector. This is a running system. Im gonna try an check the baud rate an hope for the best.
|
5/23/2014 8:42 AM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello Please have a look at this thread : SImatic S7 PC Adapter USB 6ES7 972-0CB20 0XA0 This will solve your problem. You can prepare a special cable to provide external 24VDC to the PC Adaptor for operation at nodes where 24VDC supply is not available on Profibus Connector. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
5/23/2014 8:59 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello Navnag, That not the case here. Because you can connect PC adapter to DP sockect of any S7-300 CPU. Using external power supply to provide PC adapter by 24VDC is applicable only in case the device you would like to connect doesn't provide 24VDC between pin 7 (+24VDC) & pin 2 (0VDC). In this case only you will need to use external PS. And Siemens have PS dedicated for PC adapter "6ES7972-0CA00-0XA0" But again it's not the case here.
|
Ayman Elotaify |
|
5/23/2014 10:28 AM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello Ayman Elotaify I wrote this post as the user has mentioned that he is trying to connect the PC Adaptor to the Profibus Connector on the OLM ( Not CPU !! )
CPU does not have a Connector with PG interface. The connector cannot be changed as system is in operation.
I fully agree with you if he is connecting on the CPU Profibus / MPI Port. Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
1 thankful Users |