9/12/2008 3:14 PM | |
Posts: 487 Rating:
|
Did you try putting PLC to run from the mode switch on CPU? If yes, can you post info from Diagnostic buffer? |
Last edited by: JMJ at: 9/12/2008 5:28 PM |
|
6/27/2013 6:11 PM | |
Posts: 81 Rating:
|
Dear experts, I have S7 H station 414H CPU. In those CPUs, rack 0 CPU is working perfectly but rack 1 CPU is not going to RUN mode. 1. I reseted memory through hardware as well as through software. 2. Download individually as well as at both time in both CPUs. 3.When i went to start through warm/cold restart, it shows THIS ACTION IS NOT PERMITTED even my switch is in RUN position only. Please find attchment WARM RESTART PAGE NO 2 When i clicked on HELP this page got open. Please find attchment WARM RESTART WARM RESTART PAGE NO 1. It is not going to RUN even after memory reset. what will be problem?? regards, manoj
AttachmentWARM_RESTART.pdf (1099 Downloads) |
6/27/2013 7:37 PM | |
Posts: 81 Rating:
|
Hello, I have done downloading in both PLCs. But it is not going into start mode. Please find attachment, it shows diagonstics & help of the same. It is showing I/O error but same programe is getting downloaded in rack 0 CPU. There is no problem in programe as well as in hardware configuration. It is perfectly running in rack 0 CPU. regards, manoj
AttachmentDiag.pdf (1129 Downloads) |
6/28/2013 6:32 AM | |
Posts: 81 Rating:
|
Hello Mr. kumar You are correct, we have to downlad in master CPU & slave CPU gets cordinated with sync cable & gets started automatically. regards, Manoj
|
6/28/2013 6:35 AM | |
Posts: 81 Rating:
|
hello amit, I think you didnt find attachment in my last post. I have mentioned in that all this info Please find attchment regards, manoj
AttachmentWARM_RESTART.pdf (626 Downloads) |
6/28/2013 7:07 AM | |
Joined: 9/16/2011 Last visit: 6/20/2024 Posts: 291 Rating:
|
Dear, DS SURESH KUMARis absolutely right, we need not to download the program in both PLC, it should be downloaded in rack-0 PLC ONLY. And on connecting the FO patch cord between the plc, the rack-1 PLC will sync with the rack-0 PLC automatically. But one more thing to be noted here is that it may few minutes (i.e 5-10 min) to sync depending on the program size. so my advise tohexeis, First download the program only in rack-0 PLC, while turning off the rack-1 PLC or by disconnecting the FO patch cord. After downloading, kindly turn on the rack-1 plc or connect the patch cord. Wait of sometime to synchronize. Reg, Ashish
|
Reg, |
|
6/28/2013 8:21 AM | |
Joined: 11/18/2010 Last visit: 8/5/2022 Posts: 523 Rating:
|
hi suresh, we have to download HW configuration to both PLC not software? regards, viral |
6/28/2013 8:49 AM | |
Posts: 81 Rating:
|
Hello Mr kumar, yes i am at site. I just changed slots of both CPUs & CPs. I download hardware in stop mode but still there is no result. plz find attachment of our backup regards, manoj
AttachmentH_SYSTEM.zip (664 Downloads) |
7/1/2013 7:49 AM | |
Posts: 81 Rating:
|
Hello, Now it is creating some unknown trouble for me, it is again not going to RUN mode. It is showing some SFB 20 problem. please find attchment.What is that?? I am tired to work on this PLC. regards, manoj
AttachmentPLC-pic.pdf (636 Downloads) |
7/8/2013 9:17 AM | |
Posts: 515 Rating:
|
hi, for an H station you need to download the only hardware configuration to both the CPU's whereas you only need to download the program to one CPU.
|
7/9/2013 11:43 AM | |
Joined: 9/16/2011 Last visit: 6/20/2024 Posts: 291 Rating:
|
HAS THE PROBLEM SOLVED ?? Reg, Ashish
|