10/19/2012 12:51 PM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
Hello. You can make a backup of parameters using DriveMonitor, but it will be better to take backup from drive that is not running (main contactor is switched off). Download latestDriveMonitorand install it, during installation, check that Simoreg is selected for installation.
|
10/23/2012 5:59 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, X109, 110 is for main line contactor application. Have you connected emergency switch. please refer attached sheet drawing for emergency switch connection & confirm. DEEP. AttachmentC:\Documents and Settings\ntguest\Desktop\Line contactor operation.pdf (607 Downloads) |
10/25/2012 12:08 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, In order to pick up the main line contactor, XS 105 &106 terminal must be short, either by short link or thru emergency switch. In my earlier post, Isuggested you to check this. Please refer the function diagram sheet G117, (attached in my earlier post), connection of emergency switch in two different methods is explained. Please refer it. Moreover, please see attached here with the operating display status which shall help you to understand the operational sequence of drive. PLEASE CHECK XS 105 & 106 TERMINALS FOR SHORT. THEN & THEN LINE CONTACTOR WILL PICK UP. AttachmentC:\Documents and Settings\ntguest\Desktop\Operating status display.pdf (975 Downloads) |
10/26/2012 7:44 AM | |
Joined: 1/26/2007 Last visit: 7/29/2025 Posts: 123 Rating:
|
hello , i shall check this . Thank you a lot . |