Hi, I've got an LR250 transmitter and RD100 display which are to be connected with 24DC power supply, based on loop back power (HART protocol compliant) A slight confusion on the wiring diagram which are attached. The first one is from SIEMENS web based documentation and show the -ve of the transmiiter connected with the +ve of RD100. However, te second diagram which came along the instrument documentation show the -ve of transmitter connected to the -ve of RD100. Logically, the conncetions should be like this. From +ve of Power supply to the +ve of transmitter, then from -ve of transmitter to the +ve of RD100, and finally from -ve of RD100 to the -ve of P.Supply. Please suggest so that the instruments work perfectly. Attachmentdig.pdf (455 Downloads) |
12/7/2018 9:58 PM | |
Joined: 8/9/2016 Last visit: 8/20/2025 Posts: 71 Rating:
|
Thank You for the feedback danw. I'll post after testing |
12/18/2018 3:30 PM | |
Joined: 8/9/2016 Last visit: 8/20/2025 Posts: 71 Rating:
|
the Diagnositc Status of the AI cards is also attached |
12/18/2018 8:26 PM | |
Joined: 3/28/2010 Last visit: 9/3/2025 Posts: 1170 Rating:
|
Your sketch looks OK. [snip] I'm guessing that the internal resistance (current inputs are 25 ohm resistance)
[snip] must be 'switched' into the input circuit when Mode D is selected because there does not seem to be any mechanical means of switching in the resistance. [snip] >However, when AI is looped ( as shown in attached fig.) there is no display in the field instruments, and the AI channel shows a reading of -32768. Does that mean that when the AI is wired into the loop, that the level transmitter goes dark (fails to operate) and the RD100 goes dark (fails to display values)? Hopefully, the board is still functional given the warning about applying voltage when the input is configured for current. Attachmentimages.zip (364 Downloads) |
Last edited by: Jen_Moderator at: 12/19/2018 9:02:05 AMRemoved links and added files as an attachment. |
|
12/24/2018 6:22 AM | |
Joined: 3/28/2010 Last visit: 9/3/2025 Posts: 1170 Rating:
|
I have some experience with Siemens field instruments, but no experience with Siemens PLC's or their analog cards. But I poked around and found Siemens' tutorial on 4-20mA inputs.
|