Hello ! I hope you have already solved this. This fault is normal after you have powered off and removed the cards from the rack. With the OP7 you need just to recalibrate the zero values. Go te Service menu, test mode P52 = 200, default password is 999. After that make shunt calibration by selecting P52 = 245. After do you finish set back P52 =0 Then you are done Good Luck ! Attachmentfault.pdf (500 Downloads) |