8/14/2018 12:41 PM | |
Posts: 2 Rating: (0) |
Hello, I want to connect Potentiometer 10K ohm With 6ES7134-4FB01-0AB0 Analog input card,Please help me How to connect. Regards Mohsin ------------------------------------------------------------------------------------------ |
Last edited by: AutoGen_879697 at: 8/14/2018 12:42:37 PMLast edited by: Jen_Moderator at: 8/15/2018 9:35:05 AMNew subject after splitting |
|
8/15/2018 1:01 PM | |
Joined: 5/6/2010 Last visit: 6/2/2024 Posts: 1966 Rating: (274) |
Hello, the best way is you use a signal conditioner for potentiometer and connect them to your module. Then can you connect the voltage output of the conditioner to the M0+ (1) and M0- (2). regards |
8/16/2018 11:58 AM | |
Joined: 4/23/2015 Last visit: 6/12/2023 Posts: 168 Rating: (9) |
Hello, 1. At your diagram when you turn your knob to max, you apply 24V to your AI. So you have to use additional resistor in series which limits max voltage to 10V 2. With the above mentioned limitation resistor, this will be working. But you should be aware, that when you use this approach, the accuracy of the resulting signal dramatically falls. Now it depends also on the accuracy of you 24V PS, which is generally low. I would say, you can use your approach if the accuracy of +/-8..12% suits you. The normal way to read the potentiometer value is to use a dedicated potentiometer converter (conditioner, as has been said above), which can be a standalone (converts a potentiometer signal to a normalized e.g. 0..10V with declared accuracy), or a dedicated PLC module with resistor reading function (e.g.6ES7331-1KF02-0AB0). The alternative way is also to supply a potentiometer not from a general purpose 24V PS, but from an accurate 10V reference voltage (I don't know if there are standard devices of this kind) |
This contribution was helpful to2 thankful Users |