Hello, as in case of a line fault or other fault the smart line modules "in operation" feedback at the motor modules p864 is withdrawn, the motor modules would react with F07841, which has the standard reaction OFF2 (coasting down). So you can either change the fault reaction or the feedback signal at p864. Additional you should refer to the example for OFF3 in case in line fault in the S120 drive functions manual chapter 12.4, there is shown how to prevent from coasting due to undervoltage fault., |