8/9/2021 9:10 PM | |
Joined: 10/31/2011 Last visit: 4/8/2025 Posts: 400 Rating:
|
Dear all, We have installed active interface room linked with active line module(ALM)6SL3100-0BE23-6AB) connected with three sinamics drives via bus bar. ALM r26 shows 600v but drives show 318v and the actual multimeter also measures 318v. Please guide us to the solution of the issue. AttachmentDC link of ALM and drive.zip (268 Downloads) |
Last edited by: daad at: 08/10/2021 10:11:04 |
|
8/10/2021 9:40 PM | |
Joined: 10/31/2011 Last visit: 4/8/2025 Posts: 400 Rating:
|
please reply |
8/11/2021 5:24 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Attached zip folder is empty, so could not see the which files are attached. BTW, r026 displays voltage which is scaled to reference voltage value set in p2001. So check the value set in p2001. In case with ALM, please check value set in p0210 i.e. it is preassigned device supply voltage, as a reference value. If both above checks are OK, you need to refer FD 5730, 8750, 8850, 8950 of this manual & check repsective BICO connections. HTH |
8/15/2021 9:25 PM | |
Joined: 10/31/2011 Last visit: 4/8/2025 Posts: 400 Rating:
|
thanks for the reply. This manual is not opening please resend. |
8/17/2021 6:51 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
SINAMICS S120/S150 List manual download & check. |