Hello Bramho what do you want to do exactly? So you want to load a WinCC Advanced Rutnime... -> if you only use the Advanced RT without any special Simatic Net devices then you do not need to download the PC station itself (Also you would need a siamtic Net installation and pc Station configuration). If you only use the WinCC Rutime you do not need this. Set up your project like this: https://support.industry.siemens.com/cs/ww/en/view/89852595 Then just load the WinCC advanced RT. (open Runtime Loader on the RT System and then load to the PC just as on a comfort Panel) You do not need any network shares or similar. If you use another WinCC Version like WinCC Unified or WinCC Professinoal RT then you should tell us then the answer is slightly different. Bye Murof |
|