(0)| 4/27/2023 5:19 AM | |
|
Joined: 1/21/2013 Last visit: 1/19/2026 Posts: 4410 Rating:
|
Hi EE.Stin, I assume you mean the analog input SM 1231, 4AI 16bit (6ES7231-5ND32-0XB0). This module would be fast enough to provide a new value within 100ms, so the module itself would not be the cause of the effect you are seeing. However, you should make sure that the PLC itself delivers a new value to the panel at least every 100ms. The easiest way to do this would be to use the trace functionality to sample the cyclic interrupt OB responsible for your value. You should also be aware of using a peripheral access within the OB or assigning the input addresses to the OB to get the process image updated each time the OB is called. Kind regards |
| 4/27/2023 3:18 PM | |
|
Joined: 9/21/2012 Last visit: 1/18/2026 Posts: 4853 Rating:
|
The HMI communication over Profinet is not cyclic, it's acyclic. The minimum update rate is 100ms for the HMI tags. |
| 4/28/2023 12:50 PM | |
|
Joined: 8/3/2009 Last visit: 1/19/2026 Posts: 16644 Rating:
|
Hello EE.Stin if the 100ms aquisition cycle of a live trend value is too slow (you will never get 100% 100ms; there are a lot of variation possible in HMi communication) you could use bit triggered trends with buffereing in the PLC. Here is an example (the FAQ is for WinCC flexible but in TIA its also possible quite the same way) https://support.industry.siemens.com/cs/de/en/view/21913875 Bye Murof |
|
If this Information really helps, you could use the Rate function |
|