Hello, Additional question: I know that for RT Advanced data logs limitation is 500.000 data records. But, is this limitation valid only per log, or for all logs together? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/04/2023 09:44:27New subject after splitting |
|
| 12/4/2023 3:52 PM | |
|
Joined: 5/30/2022 Last visit: 1/20/2026 Posts: 634 Rating:
|
Hi madnesssm, As you can see, the limit of 500,000 records is per log: WinCC Runtime Advanced (RT Advanced) |
|
If this information really helps, you could use the Rate function. |
|