(0)| 12/13/2023 12:02 PM | |
|
Joined: 5/6/2022 Last visit: 1/15/2026 Posts: 589 Rating:
|
Hi Jae04, A question, does it happen only with these 3 I/O fields or with all of them? If it is with those 3 I would first check in the PLC the value that the variable associated to the I/O field has at that moment. If it is correct in the PLC, then I would check in HMI the address to which it points. I would also create an I/O field from zero, no copy paste. If it is with all I/O fields then it is a communication failure. Best regards! |
|
If this Information really helps, you could use the Rate function |
|
| 12/14/2023 8:34 AM | |
|
Posts: 14 Rating:
|
Hi, thanks for your reply. I have just checked and they're down as just input (mode) I also checked the recipes and theres nothing in there. |