(0)| 1/19/2024 2:28 AM | |
Posts: 3 Rating:
I have issue, I have re-installed on a configured UPS1600 system six new UPS1100 modules however what I am normally used to the communication automatically being established and LEDs on the UPS1100 going green. However this time the UPS1100 module LED did not light and 24 hours later I still have no communication with the battery modules. I have checked the both the power and signal wiring and they are correct. Is this an issue of the UPS1600 not establishing communication or the individual UPS1100 battery modules. The UPS1600 is working just no communication with the battery modules. Regards, Marc ------------------------------------------------------------------------------------------ |
Last edited by: U_90bbd655-34cb-4a69-9b6e-3136983d42b0 at: 01/19/2024 02:29:01Last edited by: Jen_Moderator at: 01/19/2024 10:31:58New subject after splitting |
| 1/25/2024 1:24 PM | |
Joined: 4/28/2015 Last visit: 1/28/2026 Posts: 30 Rating:
Hello, did you reboot the UPS1600 after changing the batteries? Greeting. |
| 1/26/2024 3:56 AM | |
Posts: 3 Rating:
I turned off the power to the UPs and then waited 10 seconds and powered it back up, still no comms to the 6 modules. Regards, Marc |