(0)| 4/24/2024 3:57 PM | |
Joined: 11/8/2017 Last visit: 1/16/2026 Posts: 361 Rating:
Hi, For your CIM 200s, can you post some info / screen dumps of how you have configured the CIM 200s, how you have configured the PX7 comms port, along with the point mapping configuration showing live values in ABT? I've attached the mapping info, which hopefully you have already. A good way to prove the comms is working (i.e. the issue lies with the PXC7 setup), is to disconnect the network from the PXC7, and connect a USB to RS485 converter in place of the PXC7, and then use something like ModScan or CAS Modbus Scanner to scan the network. Regards, AttachmentGrundfos_CIM_module_Modbus_profiles.zip (550 Downloads) |
| 4/24/2024 4:44 PM | |
Hi, Ok, to follow on from above, I've had a look back at some older projects, and there's an early version of the CIM 200 that I was able to integrate via Modbus RTU into a TX Open module. There are 2 screen dumps attached, one from the TX Open tool, and the other from ABT after the IOOPT file has been imported. You will notice that there is a difference of 1 between the register numbers between the 2 different files - if you work with the ABT screen dump, but reduce all the register numbers by 1, and try this please. Hopefully this is all of some use to you. Regards, AttachmentDesktop.zip (575 Downloads) |