Dear klina3, Did you checked that you have completed the quick commissioning wizard by entering all motor parameters (please have a look on the attached picture). And are you sure that you have finished the quick commissiong by entering 2 or 3 in P3900? As you said that the motor is cold and F0011 appers, I am agree with Graemethat you have to make motor identification. Please follow the steps in his post. Also find attached the possible causes of F0011. Regards, Attachment420.zip (277 Downloads) |
|