(1)| 10/7/2009 10:37 PM | |
Posts: 95 Rating:
Hello I am mounting some booksize and chassis motor modules in side by side mounted enclosures. I am curious about the air flow requirements. Attached is the technical sheet from the PM21 catalog. For a current size of 210A air flow requirements is 6 cubic feet per second. The question I have is, is the included fan enough to move that much air and would the enclosure onely require filters to allow air in or should I add fans/filters capable of moving this much air. Is there a technical design manual for these drives? thanks John AttachmentPages from Sinamics_PM21_2008_.pdf (459 Downloads) |
| 10/8/2009 5:06 PM | |
Joined: 6/4/2008 Last visit: 11/25/2025 Posts: 1521 Rating:
Hi John, please find attached the Sinamics S120 Cabinet Integration Manual, hopefully this should answer all your questions. Regards, Graeme AttachmentSINAMICS_S120_SH1_0907_en.pdf (486 Downloads) |
| 10/9/2009 2:49 PM | |
Posts: 133 Rating:
The attached may help answer some of your questions but if you need to design a multi-axis lineup with booksize and chassis units I recommend you take a shortcut and use the S120 CM Cabinet Module offering.
AttachmentPages from sinamics-engineering.pdf (489 Downloads) |
| 10/9/2009 4:37 PM | |
Posts: 95 Rating:
Drives_Coach Thanks! Where is the entire document? |