Hello, This is not possible with official Modbus protocol. Therefore there is S7-200 Tips and Tricks and you have TIP41. Try to look at this tip and see the attached example. I don't know if it is possible to run slave on both ports, but try to look for yourself. Its open source. Attachmenttip041b.zip (295 Downloads) |
Last edited by: Darius at: 11/24/2008 1:38 PMI looked at this example by myself and found that it also supports port 0 also. So the only way is to use 2 PLC and connect them together via port 1 for data exchange. Best regards, |
|
11/25/2008 1:32 PM | |
Posts: 11 Rating:
|
Hi, Thanks for the guidance and support extended. |