Hi, PTO Outputs of 224XP are 100kHz. You don't need a EM253. This FAQ should help you to get S110 working with S7-200. (I think you mean SINAMICS S110, not simotion?) http://support.automation.siemens.com/WW/view/en/26513850 Beware, you need a 330k Ohm (2 watt) Load resistor between PTO output and ground, if you want to control the S110. Otherwise the pulses with more then 40kHz won't detected by S110. regards |