(0)| 7/8/2010 1:36 PM | |
Posts: 2964 Rating:
Hello... What type of machine and Control is this? You can connect... IfDClink bus P600 and M600 is connteced to X181 of M500 and P500. the purpose connectingthis is DCvoltage will get discharged slowly when machine is switched off /shutdown. In running condition DC link voltage can bechecked with multimeter Ensure connection P600->P500 and M600->M500. Screen shot is attached for the reference,if it is reversally connected module will get failed. This type ofapplications can be seen in Grinding machine, when powerfails grinding wheel has retract back for that voltage requried( additional capactior module and modification in the machine data will be requried for Emergency Retraction ) Check the incoming connections supply and how it is given to the machine. Could you explain the alarms in detail.... Check it out.... Ekalavya AttachmentP500-M500.pdf (506 Downloads) |
| 7/9/2010 11:23 AM | |
Posts: 8092 Rating:
Hello, Because of frequent power ineteruptions or failuers if infeed module is triping, you can wire up R + 15 no terminal on infeed module with 1 NO PB to reset the fault. Pls see the attached page for more information. DEEP. AttachmentInfeed module reset.pdf (479 Downloads) |