(0)| 8/1/2011 5:20 AM | |
Joined: 8/25/2006 Last visit: 1/23/2026 Posts: 2221 Rating:
Hello. How do you load your ComProfibus configuration to each SS52? Using Profibus or using RS232? I think you should pay attention when loading. If you load using Profibus, before loading to SS52 you must select in ComProfibus menu 'View' the right master system (e.g. Master system<1>, look at picture "2. Master system 1.jpg"), this is correspond to the master rack (in my example), and load to the SS52-master. Then you must select Master system<3> (look at picture "3. Master system 3.jpg") and load to the SS52-slave. If you load using RS232 you must create beforehand 2 separate .2bf files for each rack (again using menu 'View', switch between master/slave), and then load this two files to different SS52. I'm not sure, but I think you should also pay attention for address areas in slave properties in ComProfibus configuration. As I remember this areas should be filled (look at picture "4. Address areas.jpg"). I think your problem is that you load the same configuration (configuration for master rack) to the both SS52, that is selected by default in ComProfibus (look at picture "1. Network veiw.jpg"). AttachmentSS52.zip (384 Downloads) |
| 8/1/2011 4:35 PM | |
Posts: 9 Rating:
Thanks for the information regarding the ComProfibus setup. |