dear experts i wanna know that the cpu 313c-2dp supports the process image or not, to read the analog input through profibuus adaptor module (RPBA-01) thanks |
| 8/29/2011 1:21 PM | |
|
Joined: 3/21/2006 Last visit: 1/10/2026 Posts: 10247 Rating:
|
Hello, Yes, it supports PIP. Just the number of process image partitions available depends on the CPU used! Take a look at http://support.automation.siemens.com/WW/view/en/18325417 In order to read from Profibus slave there use a SFC14 and SFC15. Best regards, Hristo Mihalev |