(1)| 10/19/2011 9:56 PM | |
Joined: 1/28/2009 Last visit: 1/5/2026 Posts: 6892 Rating:
Dear habbalmg Please note that the Ti and Td parameters selected for the controller are not suitable.If you select small value for integration time, the integration part at each execution cycle is proportional to (1/Ti) which is a big number and accumulation of these values may lead the LMN saturate to high value.You can set initial value selected for Ti and Td(and Tm_lag) or use tables for tuning provided in this book. Also you have option of using valuable information shared by Forum's members here( PID tunning.zip ).About the 2nd question, you find a helpful discussion here. BUMPLESS PID Best regards hdhosseini |