Hello all, Short question. My 313C CPU has 3 integrated pulse counters. As I understand, most of the 16 first Di and 3Do will be used by the pulse counter. See page 192 of this document: Here! My question, if I only use 1 pulse counter (channel 0), do I still need to reserve all the inputs and outputs? Ton |
| 8/18/2011 9:28 AM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
If only one counterchannel isused the other onboard i/o can be used digital, see attached part of the manual. All other channels must be set to not configured. Regards, Marcjan Attachmentforum313c.pdf (647 Downloads) |
|
Problem solved? |
|
This contribution was helpful to
|
|
| 8/18/2011 9:48 AM | |
|
Joined: 4/20/2007 Last visit: 1/2/2026 Posts: 731 Rating:
|
Great! Thank you! |
| 4/2/2012 7:13 PM | |
|
Joined: 4/20/2007 Last visit: 1/2/2026 Posts: 731 Rating:
|
Please find attached the screenshots. I don't think the problem is there tho. I think its because of the speed of the pulses + the length of the cable... But I am not sure.. Thanks!
Attachmentcounter.pdf (512 Downloads) |