Hi all. I have a question regardingData exchange broadcast - slave to slave communication between two Sinamics drive modules. These two modules are connected to the PLC via Profibus. We have to change data between two drive modules in a very high speed - so we ant to use slave to slave communication on Profibus. We set the data exchange broadcast - we set communication with 10 words In/Out (see attached file image). One word we set as data exchange broadcast. Data communication is working (we can see it in Scout, when we can see data In and Out of these two drive modules). But we only can set data out PZD1 (it can be seen indata exchange broadcast overview). How can I change PZD from 1 to 10 (instead PZD1 to PZD10). In other words: how can I change PZD adress in Publisher (attached image PZD address). I cannot change it now... Thank you for any experience reagrding this. Thank you. Georgio AttachmentDP_SlaveProperties.zip (198 Downloads) |
Georgio |
|
3/20/2013 1:18 PM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, you must configure a additional input Slot on the partner CU. regards Christoph |