6/24/2013 2:27 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Follow this link. Download manual, refer chapter faults & alarm. |
Last edited by: PISCEAN 2010 at: 6/24/2013 2:28 PM |
|
6/24/2013 8:50 PM | |
Joined: 7/8/2009 Last visit: 6/7/2025 Posts: 1977 Rating:
|
Just a small confusion - your MLFB shows your drive is CU2 but you said you tried to change Parameter 60 from 7 to 5 which is of CUVC - please confirm whether your control card is CU2 or you have upgraded to CUVC I assume its CUVC so Now F011- Please refer Manual for CUVC - its overcurrent fault so you must check Output cable, motor and all Without load, you got F012 - which is quite obvious because you may using Vector control mode and in this mode, without motor, you will get this fault If you are using close loop control mode, then F011 can be because of Encoder too Please refer following to check whether it is because of encoder or not Trouble shooting in Vector Control Mode regards, Devesh |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
6/30/2013 11:09 AM | |
Joined: 7/8/2009 Last visit: 6/7/2025 Posts: 1977 Rating:
|
Hi Vijay Its not confusing. Actually i got it from this forum only check hereA very good explanation by Tambe his post will clear all your doubts Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|