(0)| 3/25/2014 7:06 PM | |
|
Joined: 11/21/2007 Last visit: 1/8/2026 Posts: 2327 Rating:
|
Hello lolo1234 You are on the Right Track !! The FB 30 is being called with Timer Value = DW 15 = KT 45.2 = 45 Sec. KT Timer format is defined as follows : xxx.y xxx = Time Value y = Multiplier y = 0 : 10ms y = 1 :100ms y = 2 : 1 Sec y = 3 : 10 Sec Therefore KT 45.2 = 45 x 1 Sec = 45 Sec. So FOUT is switched on 45 Sec after the defined condition of timer triggering ( Exclusive OR of UITG ( Q1.2 ) and ING ( I6.2 ) is satisfied. i.e. ifONLYONE out of Q 1.2 and I 6.2 is High then F45.4 will be High after 45 Sec. Hope this helps Cheers Navnag |
Last edited by: Navnag at: 3/25/2014 7:09 PMThere is no such thing as the last bug in a program |
|
| 3/26/2014 8:45 AM | |
|
Posts: 47 Rating:
|
Thank you very much it helps a lot |