3/20/2015 10:00 PM | |
Joined: 9/27/2006 Last visit: 9/10/2025 Posts: 12405 Rating:
Hello Hike; If you are willing to put a little effort in it, this introduction to explosion protection and standards should be a good place to start: SIMATIC Principles of Explosion Protection You will find there descriptions of explosive area nomenclature, protection levels and standards. For example: Then you could continue by having a look at some Siemens EX IO modules, in this case for the ET 200M Platform: SIMATIC Automation Systems S7-300, ET 200M Ex I/O Modules Hope this helps, Daniel Chartier |
This contribution was helpful to
2 thankful Users |
3/31/2015 7:22 PM | |
Hello Hike; The only such module I know of is the SM 326; DI 8 × NAMUR (6ES73261RF000AB0): The SM 326; DI 8 × NAMUR is part of the SIMATIC S7 Ex digital module family. It is to be used in compliance with installation guidelines for SIMATIC S7-Ex digital modules. The reference manual provides detailed guidelines for the configuration of SIMATIC S7-Ex digital modules.
SM 326; DI 8 x NAMUR with diagnostic interrupt , 6ES7326-1RF00-0AB0 , as of product state 05 SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modules Hope this helps, Daniel Chartier |
Follow us on