Dear all, Can anybody tell me how to write any safety program in S7-300F2 PN/DP PLC,i want to do one project on profisafe.??? |
| 3/4/2016 6:03 PM | |
|
Posts: 1410 Rating:
|
This is a simple safety program. It has 3 e-stop buttons (red mushrooms) a control voltage key, light barier, doors. Feedback for control voltage contactor, reset button, two VFD on profisafe. When all mushroom keys are released, the main output goes on automaticly without pressing reset key. If doors are closed, key is inserted and lighrt barirer free and main output on, then when pressin reset button the control voltage contactor is powered on (with feedback contact) and VFD are also enabled. AttachmentFB100.pdf (433 Downloads) |
| 3/4/2016 11:13 PM | |
|
Joined: 9/27/2006 Last visit: 1/20/2026 Posts: 12481 Rating:
|
Hello ssamber; If you are looking for more detailed information on how you develop an F-program, to supplement Marko's excellent sample, have a look at these documents: S7 Distributed Safety Getting Started https://support.industry.siemens.com/cs/ww/en/view/19810812
Safety: Safety position, standstill and direction detection and monitoring safely limited speed (SLS) on the basis of Distributed Safety https://support.industry.siemens.com/cs/ww/en/view/49221879
SINAMICS S: Speed control of a S120 with SIMATIC S7-300/400F (STEP 7 V5) via PROFINET/PROFIBUS with Safety Integrated (via PROFIsafe) and HMI https://support.industry.siemens.com/cs/ww/en/view/68624711 Hopoe this helps, Daniel Chartier |
Last edited by: dchartier at: 3/4/2016 11:14:30 PM |
|