(2)| 3/2/2018 1:45 AM | |||||||||||||||||||||||||||||||||||
|
Posts: 199 Rating:
|
Hi, Take a look to the manual, if this wiring is possible you will find it on the manual. https://support.industry.siemens.com/cs/ww/en/view/17473828 https://support.industry.siemens.com/cs/ww/en/view/18971030 Also, Be carefull it's possible to find the" same" wiring (nearly the same) on the manual but it does not comparison with "current loop" but with "line compensation". |
||||||||||||||||||||||||||||||||||
Last edited by: snoop13014 at: 3/2/2018 1:50:49 AMLast edited by: Jen_Moderator at: 3/2/2018 8:04:02 AMOptimized links. |
|||||||||||||||||||||||||||||||||||
| 3/2/2018 11:35 AM | |||||||||||||||||||||||||||||||||||
|
Joined: 8/30/2016 Last visit: 11/20/2025 Posts: 16 Rating:
|
Thank you, snoop. Looking into it. I forgot to mention that what I wanted to achieve is without program intervention, I wanted to have the same 4-20 mA reading on both input terminals from the same transducer as the other one is broken. |
||||||||||||||||||||||||||||||||||
| 3/2/2018 11:58 AM | |
|
Joined: 9/27/2006 Last visit: 1/20/2026 Posts: 12481 Rating:
|
Hello kralccvyu; Current inputs have a very low impedance. To protect them with applications such as yours, a signal isolator (or splitter) is generally recommended. https://support.industry.siemens.com/tf/us/en/posts/connecting-0-20ma-analog-signal-between-2-plc-s/184728/?page=0&pageSize=10 Hope this helps, Daniel Chartier |
This contribution was helpful to
|
|
| 3/3/2018 10:11 AM | |
|
Joined: 5/6/2010 Last visit: 1/18/2026 Posts: 2047 Rating:
|
Hello kralccvyu, the part at this link is useful to solve your challenge Signal duplicator - MINI MCR-2-UNI-UI-2UI-PT - 2905028 You have 1 input and to isolated outputs. Hope this is helpful. |