4/20/2012 7:30 AM | |
Joined: 9/28/2005 Last visit: 7/24/2025 Posts: 2957 Rating:
|
Hi, Also try to look here Which options are available for assigning the PROFINET IO controller a new IP address? |
Best regards, |
|
5/1/2012 3:41 AM | |
Posts: 1064 Rating:
|
what ip and subnet are your plc and pc at .it should work with the plc available |
5/1/2012 8:09 AM | |
Joined: 12/1/2009 Last visit: 7/14/2025 Posts: 672 Rating:
|
Dear Zer0, if you have changed the IP's of your PLC's you might have to change the IP of yourPG/Laptop as well in order to be able to access them. All devicesneed to be on the same network. You can easily check this with the ping command from the cmd window of your computer. i.e. address of PLC-1 is "192.168.2.101" ping 192.168.2.101 If the PLC-1 isreachable you should get a positive reply without timeout. Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to
1 thankful Users |
5/1/2012 5:56 PM | |
Joined: 5/6/2010 Last visit: 8/28/2025 Posts: 90 Rating:
|
Is it possible to initially program/setup the CPU315 2-PN/DP with ethernet (not DP or MPI).? |
5/1/2012 6:12 PM | |
Posts: 1064 Rating:
|
yes you can using iso protocol and the mac address |
5/2/2012 8:58 AM | |
Posts: 947 Rating:
|
you can also use TCP |