3/7/2012 10:12 AM | |
Posts: 23 Rating:
|
I'm sorry but i dont found this menu go to location. |
3/7/2012 10:15 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
|
3/7/2012 10:26 AM | |
Posts: 23 Rating:
|
THANK YOU it means the FC35 is used 14 times with the same parameters in all the program ? |
3/7/2012 10:32 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Dear MEDALI, Same parameters , I think it is impossible because different control loops have different dynamics and they need somehow unique PID parameters.To be sure, please check parameters related to each loop stored in the corresponding data blocks.You can check data for each loop while you are online to PLC.Loop parameters can also be changed via HMI. Make variable table for each loop like I did here(3-6-2012 9-06-32 AM.jpg) Best regards, Hamid Hosseini |
Last edited by: hdhosseini at: 3/7/2012 10:37 AM// Link to previously uploaded picture added |
|
3/7/2012 10:57 AM | |
Posts: 23 Rating:
|
I tried... |
3/7/2012 11:07 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
If we exclude gain(real), other parameters are of data type"TIME" |
3/7/2012 11:12 AM | |
Posts: 23 Rating:
|
OK |
3/7/2012 11:26 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Dear MEDALI, I have checked the PID parameter of your loop.For me a D parameter in order of milliseconds is really strange If D part is selected Does your loops corresponds to this parameters work properly? Also,small integration time is somehow strange,But check the real loop performance. For tuning loops refer to this link: PID SELF TUNER
Best regards, Hamid Hosseini |
3/7/2012 11:33 AM | |
Posts: 23 Rating:
|
I USED S7-PLCSIM AND NOT A REAL PLC. |