9/15/2021 11:23 AM | |
Joined: 4/28/2015 Last visit: 5/16/2025 Posts: 1278 Rating:
|
Hi again, using Technology objects is really a good idea because the handling and programming is quite simple with the Motion functions such as MC_Power, MC_MoveAbsolute,... The reason why you can't see telegram 111 is because you first would need to activate the function module EPOS on your drive - then telegram 111 is available and makes sense for that purpose. But if you want to go for Technology objects you rather use telegram 105. So which telegram you use always depends on the application task. Attached you can find a document that I personally created and it describes the most relevant SINAMICS telegrams in my opinion - maybe this brings a little more understanding and helps. The complete list of telegrams and their structure you will find in the official S120 list manual. AttachmentSINAMICS Telegrams.pdf (998 Downloads) |
Best regards, |
|
9/15/2021 3:38 PM | |
Joined: 1/18/2021 Last visit: 8/3/2023 Posts: 31 Rating:
|
Nice! Thank you! so one more question, using technology objects I should not use the basic positioner because? Joanna |