2/20/2013 8:22 AM | |
Posts: 17 Rating:
|
i can tell, dont use contactor, you must use solid.state relay |
2/20/2013 9:19 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, For S71200, and if you have only one active heating element to control temperature, you can use "PID Compact" of STEP7 Basic with PWM output (output_PWM).In this case ,PLC tries to map the analog output of PID controller via an digiatal output with pulse width modulation algorithm.More information is available in the attachment or check the following tip: TIPS for PID (FB PID_Compact)Best regardsHamid Hosseini AttachmentPID_COMPACT.pdf (1434 Downloads) |
Last edited by: hdhosseini at: 2/20/2013 9:21 AM |
|
This contribution was helpful to
1 thankful Users |
2/20/2013 3:24 PM | |
Joined: 8/15/2011 Last visit: 1/14/2022 Posts: 3 Rating:
|
Hello to all. For a plant laboratory where I have to control 16 zones of heating and the working temperature ranges from 30 ° C to 300 ° C I created (after on the PID has sent me so many times in the PLC stop) an FC in order to control the temperature. The system works by 10 months the temperature change with the right settings and 1 ° C up to 300 ° C and not to ever give you problems. gemini67 AttachmentTEMP_CONTROL.zip (1355 Downloads) |
This contribution was helpful to
1 thankful Users |
5/21/2016 6:41 PM | |
Posts: 5225 Rating:
|
@Jav Pinz: @AutoGen_924782: As alternative - attached is a PDF print-out made from TIA Portal V11 for you to study. Ihave not studied the code myself and have no opinion on how it was coded. w AttachmentTEMP_CONTROL.pdf (761 Downloads) |
Last edited by: William_B at: 5/21/2016 6:42:48 PMTweaked format |
|