4/8/2013 12:51 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Saggy; Since I cannot recognize the part number you are showing for your relay, it is difficult to give you straight information on the subject. And sincemost of myexperience with Siprotec relays lie with Profibus-DP communications, this is the bestinformation I can provide. First thing, remember that Siprotec relays are not a product of Siemens Automation and Drives (which hosts this forum), but is developped by another division, Siemens Energy. The divisions do not share ressources, so all information we can give you comes from the manuals they publish on the web. Start by having a look at various threads on Siprotec relays available on the forum: https://support.automation.siemens.com/WW/llisapi.dll?query=sipotec+profibus&func=cslib.cssearch&content=adsearch%2Fadsearch.aspx%3Ftab%3D2&lang=en&siteid=csius&objaction=cssearch&searchinprim=_searchinprim_&nodeid=99&x=16&y=8&cssearchengine=NEW&x=0&y=0 Downloads of Profibus mappings ans gsd files for Siprotec relays. “Search Keywords” tab, language: English ,” Profibus” |
Last edited by: dchartier at: 8/28/2013 9:42 PM |
|
This contribution was helpful to
1 thankful Users |
4/8/2013 4:05 PM | |
Joined: 11/8/2011 Last visit: 3/7/2025 Posts: 387 Rating:
|
thank you very much for you reply dchartier The relay part number i am using is 7SJ62 - 7SJ6231-5EB90-1FE4+L0A But in the link you sent iam not able to find GSD file Thanks in adavance |
Last edited by: Saggy at: 4/8/2013 4:11 PMLast edited by: Saggy at: 4/8/2013 4:11 PM |
|
4/8/2013 6:22 PM | |||
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello saggy; Try these links then: 6MD63, 7SJ61 / 62 / 63 / 64 Bus mapping (C53000-L1840-B006-03) V2.0_us GSD-File / GSD-Datei > V 3.00 All documents downloaded from: http://siemens.siprotec.de/download_neu/index_e.htm Hope this helps, |
||
Last edited by: dchartier at: 4/8/2013 6:27 PM |
|||
4/9/2013 6:36 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Saggy; Yes, that is starting to be apparent, and you have not chosen the easiest task to start learning Profibus-DP comms, as the relays require seperate configuration (through DIGSI 4 software) and distinct data exchange mappings.. You do not need specialized blocks in the PLC to echange data with a Siprotec relay. All data is configured as "consistent over unit" which means that you can simply read all values configured through the mapping directly from the configured address (you will see these addresses in the HWConfig). You can also use SFC 15/SFC 14 to read data consistently (large amounts of data transfered at once time); the mechanism is explained in section 4.5 of the following document: Communication module - SIPROTEC |
Last edited by: dchartier at: 4/9/2013 10:53 PM |
|
This contribution was helpful to
1 thankful Users |
8/20/2013 3:33 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Saggy; What are these ports on the Siprotec relay of yours? http://www.energy.siemens.com/ecc_pool/SIPROTEC4/881f03d4-7d96-49d2-b314-01826026699e/7SJ62_Catalog_SIP_E7.pdf Serial front interfaceThere is a serial RS232 interface on the front of all the units. All of the unit’s functions can be set on a PC by means of the DIGSI 4 protection operation program. Commissioning tools and fault analysis are also built into the program and are available through this interface. Rear-mounted interfaces A number of communication modules suitable for various applications can be fitted in the rear of the flush-mounting housing. In the flush-mounting housing, the modules can be easily replaced by the user. http://www.energy.siemens.com/ecc_pool/SIPROTEC4/0bce6147-2988-4bbd-a83b-99efe39e2a3c/7SJ62-64_Manual_A6_V044001_us.pdf You have been given many links earlier in this thread, you should find much information there. The projects I have worked with do not belong to me, so I can only give you pointers to what has to be done. The following link leads tpo the Siprotec relays download area, format it as shown in the attach,ment below to locate all availab;le manuals dans pdfs on the 7SJ62 relay:
|
Last edited by: dchartier at: 8/20/2013 3:43 PM |
|
This contribution was helpful to
1 thankful Users |
8/20/2013 4:09 PM | |
Joined: 11/8/2011 Last visit: 3/7/2025 Posts: 387 Rating:
|
thanks for the reply i will go through the manual, i will check and let you know |
8/21/2013 12:50 PM | |
Joined: 11/8/2011 Last visit: 3/7/2025 Posts: 387 Rating:
|
find diagnostic screen shot |
8/21/2013 12:51 PM | |
Joined: 11/8/2011 Last visit: 3/7/2025 Posts: 387 Rating:
|
Hardware config screenshot |
8/21/2013 4:01 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Saggy; Look at the attachment, taken from the following manual (part of the documentation ^proposed earlier): http://www.energy.siemens.com/ecc_pool/SIPROTEC4/f215125d-6567-4bf0-9362-f6e6efdfab7a/pdp_7sj6263_e.pdf It reflects Mapping 3.1, 100 bytes IN, 9 bytes OUT. Try reproducing this mapping exactly in your module selection in HWConfig: continuous addresses in byte format, I addresses first, Q addresses at the end, and no consistent values selection. Tell us if the configuration is more acceptable to the CPU this way. Hope this helps, Dniel Chartier |
This contribution was helpful to
2 thankful Users |
8/22/2013 8:21 AM | |
Joined: 11/8/2011 Last visit: 3/7/2025 Posts: 387 Rating:
|
Hi dchartier , Thanks again for the reply I have configured in HW configuration IN 100 byte and 9byte OUT in the sequence addresses first IN and then OUT but still i have the same error stating CONFIG FAULT Please guide in th DIGSI software i have selected 3-1 mapping it will select the mapping data standard format or i need to configure manually Thanks in Advance |
9/13/2017 2:24 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Huyhung; All these subjects have been covered in this thread already, so it would be better if you started by reading the posts that precede yours, and opening the proposed links and documents. A few notes: a mapping is a selection of values that can be transferred to a Profibus master in a single telegram. You must select one of the available mappings before you open Digsi or Step 7, as you plan your application; note how many bytes this mapping will use over Profibus.. When you have selected how you are going to exchange data with the master, open Digsi and in the Communications area select the same mapping for Profibus-DP exchanges. Next open Step 7 and in the Profibus configuration first integrate the 7SJ62 gsd file, then drag an icon for the 7SJ62 to the Profibus master; then select as many modules are necessary to obtain the number of bytes to be exchanges with the selected mapping.(both input and output bytes). For example, mapping 3.1 requires 100 bytes IN and 9 bytes OUT. See the attachment below for a sample configuration for mapping 3.1. Ythis was copied from the following discussion: SIPROTEC Profibus communication with 315-2dp Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 9/13/2017 3:18:11 PM |
|
This contribution was helpful to
1 thankful Users |
2/9/2021 12:18 PM | |
Posts: 4 Rating:
|
All of the previously shared links are now unavailable.please help me. thank you |
2/9/2021 5:28 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello pdas; If the information you are looking for is related to the Siprotec 7SJ62 Profibus files, you can find them all here (gsd, mappings, DIGSI driver): https://support.industry.siemens.com/cs/ww/en/view/109743550 If it is for a different relay, Siemens Energy ( the Siemens division that develops, manufactures and distributes protection equipment) provides access to its documentation at the following address: Hope this helps, Daniel Chartier |