Hello Look at this sample program: reading out diagnostics of a PROFIBUS DP slave in the OB 82. Maybe will helps to solve the problem. regards |
| 2/12/2009 9:30 AM | |
|
Posts: 13 Rating:
|
I found it, i had to enable the Operation at Preset <> Actual Configuration in the IM151-1. |