(0)| 10/10/2021 3:29 AM | |
|
Posts: 2 Rating:
|
Facing same problem for 840d al control. I have tried with new NCK battery, but not worked. Have you found any other solution ?? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/11/2021 11:10:08New subject after splitting |
|
| 10/10/2021 5:42 AM | |
|
Posts: 8092 Rating:
|
Hello Viveknd, Please post your query in new topic instead of old. Significance of Alarm 300701 is START UP is required for drive. 611D drive data is stored in 840D NCU memory which is restored in 611D drive during every power ON of system. Have you restored NC data after replacement of battery? I guess in your case data is lost & you need to clear NC PLC data & restore it. Before clearing, pleas check if you have valid NC, PLC back up data either on your system i.e. HDD or NC card or on external storage device. Please refer attached sheet having information of cleraing & restoring NC PLC data. Hope this helps. Attachment840d PL NC___PLC_Data_Clear & restore procedure.pdf (263 Downloads) |