HI Every one Looking for the support on one of the shaping machine Table with sinamics drive , showing vibration as shown in the attached video I tried to set the Gain 32200 , But still no improvement . Please suggest how to diagnosos the problem AttachmentVID-20220330-WA0036.wmv (281 Downloads) |
| 3/31/2022 5:08 AM | |
|
Posts: 8092 Rating:
|
Hello CNC Chennai, Assuming it is old running machine, please check below points. 1. Does this table has motor encoder or external encoder feedback? IIf external encoder, check mechanics. If motor encoder, check drive current. 2. Assuming it is new machine under commissioning, conduct AUTO SERVO tuning, speed & position control loops. To diagnosis the problem, conduct/use trace of the axis with speed, current parameter & attach it here. Hope this helps. |
| 3/31/2022 9:21 AM | |
|
Posts: 8092 Rating:
|
which is smc? can you list parameters which you changed? what alarm displays after you change parameter? what procedure you followed when you changed parameters? Please refer Replacement of S120 componenets topic which will give you information about parameters to be changed while replacing any component in SINAMICS. |
| 3/31/2022 12:40 PM | |
|
Posts: 177 Rating:
|
Sir , Attched the SMC Details Need support on the Paramaters |